Safe shutdown of Simatic Process Historian
cardosocea
Nov 2016
Fields of corn
2,643
Hello Gents,
In one of our plants, the UPS is nearly dead and due to budget constraints, the UPS we are getting is not going to be big. So I am looking at a way to programmatically shut down the servers if the UPS drops below a certain point.
Looking in the Siemens website, I found that there is a fairly well described process to do this on WinCC servers and I already have this up and running.
However, there is no such thing for the Historian application. From what I read, Microsoft SQL server is fairly nice at shutting down cleanly when shutting down the server normally, but considering that Siemens shut down procedure stipulates that the historian software be shut down before stopping the computer leaves me a bit nervous in doing so. Especially considering that I don't have hardware where to test this on.
Do any of you had experience on this before?
Also, I looked into the hard drive cache as this is one of the points mentioned around the internet as the reason for data corruption on power loss and found that the RAID controller and Windows settings seem to be inconsistent.
What do you guys think?
Image Link
Hi guys how do you manage the shutdown of the Factorytalk View SE runtime when the UPS for the PC/IPC is running out of power? Right now the UPS...
1,853
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
159
Can somebody share the AutroSafe configuration Tool C4.11.4 Thank you
127
I have a GuardLogix PLC with safety inputs of HMI, Estops, Light Curtains, and Gates. Is it considered safe for the safety program to monitor the...
803