I'm looking for a safeload device other than using ct with analog card on a plc. current range is 10 amps. I use to remember a AB current relay w/time delay which is not longer sold? I'm not comfortable using a PLC monitoring the equipment. Your help is greatly appreciated.
 
In the terminology I'm familiar with, a "safe load" device has to do with cranes. But it doesn't sound like you're referring to one of those.

Are you talking about a conventional 3-phase overload relay, or a single-phase monitoring relay of some type ?

Describe more about the application, especially about the safety aspects.
 
the current relay in on one phase of the 3 phase after the starter. safety relay that senses a jump in current it shuts off the equipment. this equipment is a Industrial conventional Oven (tray). so its important before it tries to destroy itself?
The problem I have in the plant is no one understands the PLC. a simple device could be install and reset. Second the HMI don't display the current instinctively. this display should have a analog meter so you see the jam up.
 
the current relay in on one phase of the 3 phase after the starter. safety relay that senses a jump in current it shuts off the equipment. this equipment is a Industrial conventional Oven (tray). so its important before it tries to destroy itself?
The problem I have in the plant is no one understands the PLC. a simple device could be install and reset. Second the HMI don't display the current instinctively. this display should have a analog meter so you see the jam up.

A monitoring relay like this could be used http://www.phoenixcontact.com/onlin...14-10-01/ccbba64a-0174-4263-8175-b4d204099b69

or something that provides an analogue out. I've used many of these over the years.
http://www.synctek.com.au/LMR10a.html
 

Similar Topics

Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
60
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
111
Hi, First time poster, long time reader. I've got a mass flow controller device for controlling the flow of gas. It has a flowmeter and an...
Replies
4
Views
276
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
586
I'm adding an IAI Gateway with 2 axes connected to it. To an ethernet network on my PLC. So, I think the math is correct on the Input and Output...
Replies
0
Views
147
Back
Top Bottom