I've wired it back mainly because I haven't used a GuardLogix yet. Our safety controllers are Keyence GC-1000s that can't communicate with the drive directly. I guess I could use the CompactLogix that's talking to both to be an intermediary, but it was easier to just land a wire.
Do you need redundant load contactors? I thought I saw an example from Rockwell showing a single safety-rated load side contactor getting it to PLe.