Safety AUX contactors & Safety Relay
Ruhstko
Jul 2021
Tula
Hello colleagues! I decided to ask for advice, I hope someone has already studied the issue.
I'll try to formulate more correctly. There is such a thing - Safety Aux Contactor - for example, the WEG series CAWBS or Bulletin 700S by Rockwell.
There are also well-known safety relays. Is it possible to expand the contacts of the safety relay by connecting the Safety Aux Contactor? If we`ll switch its coil through the contacts of the safety relay.
Either it is unacceptable, because it is outside the rules and standards?
What you are suggesting is done quite frequently. Safety contactors are nothing more than regular contactors with force-guided contacts. (Apparently the red and yellow colorings for plastic are very expensive.) Since they don't have any logic of their own, they are driven from contacts of master safety relays. Just be sure to use the NC contacts for EDM feedback if your application calls for it.
AB has these expansion relays: https://www.rockwellautomation.com/...ty-relays/specialty-safety-relays/msr132.html
Which are supposed to expand the MCR output to other output circuits, as if they were connected directly to the MCR.
I'm not sure how much cascading is allowed though, I'm guessing there has to be a reasonable limit, as each cascade probably adds a time delay when the output switches, maybe someone else on the forum can elaborate.
UPD. In general, as I thought. Then the question is different. I have, for example, a Pilz relay with a bunch of outputs. How legal is it to put an external considered safety relay instead of built-in outputs?
It depends on what will turn on the external safety relay. If it is being used to expand an existing one, then tying in the EDM N/C contacts is fine. If it is being turned on by something else then jt needs an assessment to make sure that is being implemented in the correct fashion.
After some interesting conversation regarding the safety of emergency stops, I saw some posts talking about the safety standard conversation...
24
648
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
110
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
105
Hi I have a yaskawa gp7 robot arm which I am going to use for machine tending with a cnc mill. Is it a good idea to buy a SICK laser scanner for...
240
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
116