Safety RS Studio v 30,31,32 Rockwell View Designer V7.02

dahnuguy

Member
Join Date
Mar 2007
Location
SC
Posts
720
5370 PLC with a 440C CR30 22BBB safety PLC.

5 Estops wired in series back to the safety input.
Using pulse outs to power estop contacts.
2 sets of NC contacts on each estop.

Machine is new install, safety was working in shop and onsite.

Now all the safety input blocks are solid green with the SOF1 blinking slowly from grey to green as if it only needs a reset.

Give it reset, reset input goes green.

No change in SOF1.

There are also 2 light curtains and 4 scanners , each set are connected in the safety PLC using AND blocks and then all 3 sets of AND are connected to SOF1.

2 estop input blocks AND2 light curtains AND 4 scanners = SOF1

Reset input is on SMF3 and SOF1 has SMF3 input defined as its reset. SOF1 is manual reset.

Any ideas why the safety PLC will not reset? It worked for awhile. 2 different PLCs are doing this now. Was just one.

I played with increasing the discrepancy and input filters on the safety input blocks but nothing seems to make any difference.
 
No one here tonight but me.
I found that if you leave the reset button pushed for slightly more than about 1 second, the safety blocks just error and will not reset.

But if I use a shorter reset, like 500ms, the safety PLC resets but the alarm code needs to see the safety reset and also reset the alarm.
Which takes just over 1 sec.

So I used a clock bit to pulse the reset twice at less than 1 second each, for each time the reset button is pushed.

No operator is going to hit reset twice and make sure the lights turn green etc.
 
E-stop, LC, and Scanner have their own block right? Not the AND instruction, but instruction specific for LC, E-stop with pulse test.
 
E-stop, LC, and Scanner have their own block right? Not the AND instruction, but instruction specific for LC, E-stop with pulse test.

Yes they do have their own individual input blocks.
They are then ANDed to one output.
Holding the reset too long will cause the safety PLC to ignore the reset.
 

Similar Topics

Hi, I have this weird issue whenever I try to change the SNN from a Point IO Im missing the three ... dots to open the pop up and change it...
Replies
4
Views
619
Hey! Quick question. Is there a quick and easy way of recurrently move safety inputs to a DINT for example? This is the idea but for obvious...
Replies
4
Views
1,825
Hi, Short question....Is it possible to emulate a safety program that has an L72S and L72SP? I try and download this to an emulate program but...
Replies
2
Views
4,712
I created a new project with a 1756-L72S controller. Now I want to change the controller but the option to change the controller is grayed out...
Replies
6
Views
4,633
Hi all Was wondering if you guys were able to help. I am onsite trying to program a 440C-CR30-22BBB Safety relay. Using the following pdf and...
Replies
5
Views
4,385
Back
Top Bottom