Save HMI inputs to RSLogix 500 address
JuanPLC74
Feb 2017
Houston
23
I need to download a program to a micrologix 1400. Once I download it, the operator puts in some setpoint values, I need to save them to the tags they go, so If I download again, he does not have to go through the setpoint setup again. How can I do this?
thanks in advance
Go Online hit Save, Upload all Tag Values. Then Go Offline. Values for set points should be correct.
After those setpoints are entered, connect to the PLC, Go Online, and Save the PLC program. This will make the file you have saved match the entire contents of the logic and data in the PLC.
With RSLogix 500, when you download or upload and save, you get everything. Also, all data is retentive so nothing will automatically reset or change following a normal power cycle.
This keeps things fairly simple and straightforward, but if you will be frequently downloading files to the controller, it can in some cases be a headache.
If you can record the critical setpoint values in the PLC before you download, and then populate your offline file with the proper numbers, you can avoid the extra data entry. If you need to make small programming changes that don't include adding data table space or program files you can (usually) just perform online editing and then save it when you are done.
We have a OP270 Touch 10 and are trying to get a Backup using Prosave. It starts and seems to be getting Image1.img and then on to Image2.img...
4,880
Hi; First of all, I am sorry that my post is not relevant with this forum. I have recently purchased Samsung cell phone. I have alreay saved...
77
Hello! I have a datablock in a PLC witch contains about 700 variables. I must save this data once a day on a Windows PC in a XML or CSV file. Eg...
491
Hello Folks! I have an issue and its very often but in this case i applied all the tricks and tips that i always do in similiar issues but in this...
778
I'm a bit stuck again... See the redacted picture. At the moment, pressing F7 saves the "live" laser measurement into the boxes indicated by the...
1,079