Scaling Temperature Sensor(PLC S7-200)
raguilas
Dec 2015
Sinaloa
48
Hi everyone I have the following:
1.- PLC S7200
2.- HMI tp177b pn/dp 6"cstn
3.- Temp. transmitter IFM TP9237
2.- HMI tp177b pn/dp 6"cstn(image)
https://www.lagerwerk.com/elektrik-...ch-panel-tp177b-dp-6-mstn-6av6-642-0bc01-1ax1
3.-Temperature transmitter(image)
http://www.ifm.com/products/mx/ds/TP9237.htm
http://www.ifm.com/products/mx/ds/TM4311.htm
I want to create the scale so I can get the temperature value(° Celcius) on the PLC and then read the value from the HMI(tp177b pn/dp 6"cstn) and display it.
So I'm using a library called "scale.mwl"
I already have connected the temp. transmitter correctly, before doing it I cheked the voltage outup value(from the transmitter) with a multimeter and a lighter and could see the voltage variation(0-10V) as the temperature went up/down.
Now, I have no idea what variable or where I should be reading the engineering value from("32000-6400" or "32000-0"?)
I don't know wheter its going to be adressed to AIW2 or VD100.
I also have to select between three block types for scaling: S_ITR, S_RTR or S_RTI, and don't know what's the right option.
Blocks images:
http://i.imgur.com/ta9DVQX.png
The temperature range that I'm going to be using is between 10 to 60°Celcius more or less...(50°F to 140°F), I need the value in celcius :)
Could you be so kind giving me some orientation please?
Thanks in advance.
Best regards :D
Unless you have the I/O-link adapter, in which you can alter the range of the transmitter, the factory default setting is 0-10V = 0-100°C.
As it is 0-10V, your range in the PLC is 0-32000.
S_ITR will scale your input to a real (ie. floating point) value.
Addressing for the inbuilt Analog input on an S7-200 are AIW0 for the first analog input and AIW2 for the second analog input. This is where your 0-32000 integers are located.
After you have done the scaling, you will need to put it in a memory real, that is VD100 or similar. The VD100 address will contain for example 50.3°C
Hope that helps.
Hope that helps.
Thank you for taking the time to reply and helping me AustralIan, I really appreciate it, I'm taking your advice and I'll try it, first thing in the morning at the school lab.
=D
Hope that helps.
Hi AustralIan
Thanks for your help, I did it the way you told me, and it worked perfectly =)🍻
I created a memory real variable on wincc and it worked just fine, I attach pictures.
Have a great day!
Thank you once again.
Microwin
http://i.imgur.com/x7ntwNW.jpg
WINCC
http://i.imgur.com/8wRnlhv.jpg
Hi guys, It's me again with another question. I have like three projects going on and I'm going crazy. I have this OMRON E5EN temperature...
2,327
I have everything set up for vibration monitoring with the code in Controllogix 5000. The thing is that I am not able to read values SCADA in mm/s...
19
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
190
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
643
376