there is three values, minimum, current and maximum.
You should look current. Current and maximum should be much less than watcdog time, else your PLC will go halt-mode. (Watchdog overrun)
PLC have 2 different scan modes. Cyclic (free wheeling) and periodic.
Cyclic processes program as fast as possible.
Periodic means that you can have something like 100ms period for program. Logic code can still have something like 20ms scan time, but before next program scan PLC waits 80ms (80+20=100ms)
Setting periodic/cyclic is maded at offline before program downloading. It is poperties of MAST-task.