Sensor read outs
Jimbo123
Feb 2015
Sheffield
Hi all,
I have two questions. First question is I want read the values from two capacitive proximity sensors to give a read out for example min level and max level. The second question is how do I trigger an alarm when these values are met. I am using siemens step 7 and a s300 plc, to control the level of water in a tank. Is it possible to have the read out initally in the step 7 software and then after display them on the WinCC scada system.
regards
Jimbo
SO you will evaluate the input, if low becomes 0 sound alarm.
if high becomes 1 sound alarm.
you can directly add your input addresses in WinCC.
Maybe you have to elaborate on your project, or assignment if I assume correctly?
What I understand is that you have 2 digital inputs into a PLC. Say I0.0 and I0.1.
You want an alarm for each of these inputs in a HMI. Then specify these two bits as the alarms. There is no need for any functions of function blocks in the PLC since there is no logic.
Now.. If you want to add some more functionality. Say start/stop filling on these two sensors, in addition to (delayed) alarms, you might want to look at SR (or RS) Flip Flop and On (or Off) Delay Timers (S_ODT/S_OFFDT).
If this is a homework assignment, please be honest and let us know. We might not give you the code, but will help you come to it.
Hi, It is a homework assignment, What I need to do is firstly turn on an alarm at minimum level. Then at a Maximum level turn another alarm on, then with the use of a float switch use that to turn the pump off.
Can this not be done by a function for example, If input(sensor min) is 1 then turn alarm on. If input (sensor max) is 1 then turn alarm on. Or is this not the best way to address the issue
thanks
Sure, that sounds good :). I live by the KISS principle. Keep It Simple Stupid :).
Just keep in mind, that it is likely your low alarm will come when there is NO water in front of the sensor. The high alarm is opposite. Also, the alarms should have different tasks. Low is likely used to stop a pump (external?) or what ever draining your tank. High alarm should also stop filling in case your float switch fails.
Another thing is that when the level is close to a switch point, the alarm (or pump start/stop) may come and go numerous times. You might want to add a delay to counter this.
Good luck!
Good Evening , I'm looking for a moisture sensor to read muffin dough going across a conveyor . We have recipes , that should add the correct...
3,015
Hi all, For my senior design project I am controlling a large three phase motor from the program Labview through MODBUS. The sensors being used...
5,787
Hello. I've been learning about PLC's in a few months now, mainly PLC programming, and yesterday I got an assignment to read an analog laser...
4,627
Good evening everyone, Is an application I'm using a module in a HSCE2 Rockwell SLC500, but after seeing how difficult it is to work with this...
1,321
R
I am working for a bread manufacturing plant. We face one problem. I need a sensor to solve this problem. Our dows are carried in small buckets...
25
7,978