sequenced go-no-go gage
Chris-trmaint
Apr 2007
WI
Looking for a solution, we are building a fixture to test an injection molded part with 4 metal inserts. the fixure is built, just having problems with the program. Using micrologix 1000 plc. We need to test for continuity in each of the 4 inserts, but we cant have continuity between two different inserts. All we are doing is energizing one relay output at a time to activate the corresponding input and then unlatching it. I'm unsure as to how I can save that signal after unlatching that output and moving on to enegize the next output to recieve the next signal. I'm very unfamiliar with this new RSlogix software. I thought of energizing an internal relay for each signal, and then using all 4 relays to signal a green light or red light for bad part. What are the internal relay designations in this software, or is there a better way to go about it? How would I reset those relays if used?
Thanks for the time
Chris
I'm not sure on your process, but you may want a short condition, to fault out the test. Most likely if two pins are barely shorted, one of the tests will show bad, however it only takes one ladder scan to show a good part in the example above... You may miss an intermittent contact.
Good point! You may also wish to have the test exercise the contact integrity at the rated load. (See Ohm's Law to set up the load circuit voltage, current, and resistance values.)
I wouldn't run the test too hastily or you will indeed miss the intermitant problems. Run the test for whatever time is available (1/2 second?) or run multiple tests while in the test station.
Chris-trmaint said:
Thanks, that is just what we were looking for, it worked great.
Thanks for your time.
Chris
IMO, Alaric's example could use some more control reliability with respect to when the rungs for the OTLs are true. Placing a normally open contact (XIC) of the output in series with the expected XIC input would assure that the OTL instruction is energized only when its supposed to.
Example: if the timer value is 2, O:0/2 is on. If you are expecting only I:0/2 to come on and only I:0/3 comes on instead, the rung OTL B3/3 would be energized and give a false positive, a big no-no in the gaging world. To add reliability:
In rung 6 insert -| |- O:0/0 at the beginning of the rung.
In rung 7 insert -| |- O:0/01 at the beginning of the rung
In rung 8 insert -| |- O:0/02 at the beginning of the rung
In rung 9 insert -| |- O:0/03 at the beginning of the rung
That will coordinate the input response with the output.
“Sequenced Light Array Routine” RSLogix 500 Constructed by:Lancie1 In this routine, we are using some NO contacts, some NC contacts, timers...
3,130
http://www.youtube.com/watch?v=Q3x5MI9xNCQ&feature=related ...and from 04:20 this one really gets arti-tectual...
1,718
Hello, I been trying to pull the probe readings from my Metro M400 air gages through a modbus to a plc. I have a connection right now between the...
1,126
Hey guys, I Would like to create an average of an analog signal. I have a transducer feeding a 4-20mA signal to my Analog input channel for...
16
4,083
I'm a little confused about the wiring from a King Gage to a Red Lion G3 unit. We are using the MODBUS protocol from the King Gage. I took a...
2,258