Hi can anyone help me out creating a sequential alarm output
using microwin s7200
Say if you had 35 alarm bits and 5 alarm inputs are on.
i need to scroll through each alarm as long as they are active continously looping each one on for 2secs in form of output bytes.
This is just to display to an led sign .
How could i do this
I don't know how limited 200 indirect addressing is.
One method is convert this to s7 200 (Different PLC)
added 3. picture, works better
thanks but i see that example uses an array dont think its possible in s7-200 microwin
indirect addressing is an option i was looking into but couldnt figure it out. never used it before :mad:.
Could anyone provide an example
thanks
https://support.industry.siemens.co...ect-addressing-for-the-s7-200-?dti=0&lc=en-WW
Not easiest with Siemens.
How about copying 35 different values according alarm bits to word. (35 different networks)
Then counting from 1..35 with delay
If alarm bit is on and count (your index is right, copy value 1..35 to output
p.s attacment added.
M0.x = alarm bit
MW100 = index (counter 1..35 with delay)
MW200 = alarm number
hi
with that method worst case wouldn't it have to wait before it reached the same count or am I reading it wrong
TRhanks
It depends how you count your counter up. If only with 2second pulse, then it will take 70seconds to count between two different alarm states.
But if you count counter up every PLC scan and only stop it when alarm is on, then it will work as you want.
(compare mw100 to MW200, if they are equal, then count up only when delay 2second have passed.
if mw100<>mw200 then count up without waiting on every PLC cycle. Code is almost same than on attachment 3 allready.)
you also need to zero alarm output if there is no alarm bits on anymore
Hi there, We have a system at a water treatment plant where large raw water tanks feed into the plant that's all on the same level. At high tank...
18
3,811
Hi, I started off my career in PLC programming doing water/wastewater on AB around 20 years ago, but then moved overseas a few years later and...
57
12,194
It appears to me that Logix is improperly executing sheets of an AOI in sequential scans instead of the same scan as the main program. To test...
1,690
Hi, is it possible to read the name of the steps in an S7 Graph sequencer? In the parameterinterface there is, for example the parameter #S_NO...
21
7,242
Hi All, is there a way to incorporate SFC with HMI in some way, in order to represent missing conditions for next step. Something similiar...
982