Servo Drive and PLC communication...
wannalearn
Jul 2008
Georgia
16
Where do I go for good, reliable information on connecting a servo motor, encoders, and such to a PLC...?
I have a MicroLogix 1000 (1761-L16AWA) and was hoping that I could somehow use it for connecting several servo motors in a machine modification project coming up soon.
Any information would be greatly appreciated.
Thanks,
Wannalearn
Hi:
To properly give advice I feel you need to provide more information of your scope, in reference to the servos. Motion control is kind of complex. In other hand, the PLC is very limited.
I feel is possible you control a servo with digital outputs, and read status with digital inputs,but it going to be dificult to send data as setpoints or commands.
I have done servos but with the ML1100. Specifically IDT4, which is integrated servo motor-drive from AMK, this is using Modbus-RS485. They are reliable with small torque (about 4 NM).
My perception is you may need, for a little PLC, at least modbus to do something usefull.
Regards
Somewhat off-topic, sorry to hi-jack the thread:
My hardware knowledge is somewhat lacking...what is the difference between a VFD and a servo drive? Or are VFDs a type of servo?
Wannalearn,
This is a pretty broad question but I will share my experience. The fact that you are using a very low-end PLC will limit your choices. I have had good experience using a Red Lion G3 to control parameters in an Allen-Bradley Ultra3000 servo drive. The G3 could also interface with your PLC so everything could be talking together. But I would highly recommend that you look at upgrading your Micrologix.
http://www.plctalk.net/qanda/showthread.php?t=22687
Hi All, I'm using Siemens S7-1500TF plc and S210 drive for camming, more than 4 axis. anyone designed camming application with different PLC and...
1,096
1,038
Hi, all friends, I am developing an slicer machine program, where servo drive has to move 20 mm (whatever is set on hmi) distance and again it...
4,713
Hope someone can give me some advice on how this can be done. My boss wants to take a unidrive servo drive controlling a servo motor that will be...
11,150
i have a problem in communication of R7D-AP08H servo drive of omron make and CP1E PLC. the plc has open collector output of 24 volt dc and servo...
5,501