SF LED is ON on SM326 I/O module
darshana821
Jun 2009
Rochester
I have installed CPU315F with a safety protector, SM 326 DI 24 and SM 326 DO 8 I/O modules. I have downloaded the hardware configuration and CPU does not show any error. But Both the I/O modules have SF LED ON. In the module properties, diagnostic buffer shows "CRC error data message".
How can I resolve this issue? Please help.
Thanks,
Darshana K
I think the hardware configuration is not matching or check the I/O address .
Or try creating new project and upload station and then download.
Thanks for the reply, but i have checked the hardware configuration and the I/O addresses are fine. I have connected few lamps to the output channels of SM 316 DO 8 ch module. I can see flickering light through these lamps at regular interval. Is that because of the SF light or it is causing the SF LED to be ON.
I am using profinet communication. and I am using ILPBs for Start, Stop and ACK commands. The lamps are connected to SM 326 DO 8ch module and the contacts (NO/NC) are connected to SM 326 DI24. Earlier SF light was ON on both modules but now it is coming only on DO module. and as I mentioned earlier, I can see flickering light at regular interval through lamps. When I open the diagnostic buffer, CRC data error message appears.
Sounds like you could have a bad connection somewhere. Im not familiar with profinet but ive been around profibus alot and you can get very strange problems if you have a bad connection somewhere.
Sorry for my lack of knowledge, beginner here. Yesterday, we had a Pro-Face SP5000 HMI fail on us. The technician said that the HMI had the blue...
148
hello I have 7cp476 cpu why can led always open and No connection
148
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
124
Hi everyone, I got a Parker HMI, CTC PA2. I tried to download program to it but it froze in the process and could not finalize. Now, when I try to...
55
Hi all, I am trying to do Modbus communications via the CB1241 RS485 Communication Board on a Siemens S71200 PLC. I am using a 1215C CPU. After...
279