Sharing Input Data Between Different PLCs?
amir-a
Jan 2012
Melbourne
G'day All.
I am having a problem with a conveyor system which is controlled by two different Mitsubishi PLCs and below is the CPU information
Q06UDEHCPU
Q10UDEHCPU
They can be monitored through a CC-link network. The problem is that I need a sensor data sent to the first PLC to be recognized by another one. But currently it is not possible. Does anyone have an idea on how I can do this?
Tnx :)
In the A-B world we call these Messages or produced/consumed data. You may want to check if your controllers has something like this. Depending on the distance it may be easier just to hardwire a signal between the 2 processors.
I am having a problem with a conveyor system which is controlled by two different Mitsubishi PLCs and below is the CPU information. . .The problem is that I need a sensor data sent to the first PLC to be recognized by another one.
This sounds like you may be using two PLCs to make decisions for the same conveyor. That will get you into trouble fast. It is like if your body had two brains giving different orders to the same muscles. I bet that one of the PLCs only needs to know the final result of some overall set of variables. You could do this with one new output, say on PLC#1, that is wired to a new input on PLC#2.
Something I've never thought about before... maybe you folks have some thoughts or experience. I have a customer that uses a Weidmuller, Modbus...
199
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
190
Hi, We don't do many Rockwell projects but recently did onw with a Control Logix and Panelview. What files do customers expect when you send...
289
Hi, I recently acquired a micro830 48qwb, and it has relay outputs bult in. For outputs 0-6, they all use 24vdc. To save on space and terminal...
1,523
Hi, I'm challenging myself to install a PLC for the first time. I went for a Micro830 48QWB, since it has 48 I/O and free software (CCW). From my...
1,993