SICK barcode CLV6300 via DeviceNet

feniks

Member
Join Date
Jan 2008
Location
Wrocław
Posts
29
Hi
My task is to connect SICK barcode scanner CLV6300 via DeviceNet witch SLC 500.
I did not have problem with receiving data and decode barcode. i configured scanner with 32 I/O bytes. My question is how send commad to scanner for example "sMN mTCgateon".
There are 5 bytes for DigitalOutput, TelegranLenRes ..Count itp and then is Telegram.
Please help my :)
my email: [email protected]
Thank You very much
 
Problem was easy for someone who knows how send ASCII command via rs232.
First we send <STX> in hex it is 02 then command for egsample "sMN mTCgateon" ofcourse in hex so it will be 73 4d ...etc. and at the end <ETX> in hex 03. The most important things are: to increase field: OutTelegramCount after each message and send actual lenth of it.
Bye
 
Connection

How is the SICK scanner connected to DeviceNet.

By using the SICK CDx / CMx Connection Module or ??
 

Similar Topics

Hi All, On-site we currently have various CLV62x Scanners, these scanners connect via ethercat to a beckhoff PLC, We wish however to use the...
Replies
3
Views
1,788
hi, i try to connect sick clv490 barcode scanner to hyperterminal to send some command like "21" turn on laser beam. it work fine with sick...
Replies
0
Views
1,495
hi, i try to connect to sick clv490 barcode using controllogix serial port but i can get it to work. im using ascii read port 0 but nothing.
Replies
0
Views
1,214
Hi guys, I hope you are all doing well. I'm trying to connect a SICK BarCode Reader (CLV630-6120) to RSLogix in order to use it with my PLC...
Replies
3
Views
4,300
Does anyone have experience with setting up this device? I know the setup can just be done via the barcodes in the manuals. But for the life of me...
Replies
1
Views
1,482
Back
Top Bottom