SIEMENS ( 27-400 ) time stamp of digital inputs

naishadgosai

Member
Join Date
Aug 2005
Location
surat,gujarat
Posts
39
Hi,
I Have A Siemens Make S7-400 Plc.
I Want To Know ,how Can I Get The Time Stamp Of Digital Inputs Via Sfc / Sfb ( standard function blocks) Or Any Other Way.

Pls Give Feedback
 
Do you want to store the date/time that a particular digital input changed state ? (Note that time-stamp is a phrase associated with siemens code blocks) If my suggestion is incorrect, please re-word your query giving more detail about want you are trying to do.
 
Special I/Os

If i am not wrong there are special I/Os in Siemens which can have Time stamping done at I/O level (I/O Card level usually Inputs Digital), may be used for Seq of Events accurate to ms ( not sure what that value is).

With normal I/Os it may give you diff values as per scan time ( i.e. even using SFB/SFC When the SCAN ROUTINE CHECKS THE I/O status).

Just Guessing
-----
Arc
 

Similar Topics

Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
Replies
15
Views
346
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
670
Good Afternoon. I am having a problem going online with S7-400. Attached is the error that I am getting. I have looked at the help file but the...
Replies
7
Views
1,786
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
Replies
4
Views
1,508
I have a project where I've decided to put in a facility to change the PLC time and date through the HMI, as there's no network connection at the...
Replies
3
Views
1,907
Back
Top Bottom