Siemens Analog input card
rajendrad
May 2003
Pune, India
19
IN THE RECENT COMMISSIONING I HAD FACED SIEMENS MAKE ANALOG OUTPUT CARD FAILURES.WHILE CHECKING THE SYSTEM I NOTICED THAT 24VDC INPUT TO THE CARD IS VARYING FROM 19VDC-25VDC.THIS IS BECAUSE SOLENOID LOAD IS ALSO ON THE SAME POWER SUPPLY.IS SUCH POWER SUPPLY WILL CAUSE FAILUARE OF ANALOG OUTPUT CARDS ???????????
Please, turn off the capitals. WE CAN HEAR YOU!!
Now, you were using a digital meter, I'm guessing. The voltage was dropping lower, but you meter averages for short times and misses the peaks, up and down. The cards are not designed to have fluctuating power and puts a huge load on the solid state componets. The filters can't filter out everything and I guess a spike wiped you out. Seperate the power supplies.
What RRobins said is certainly accurate. A lot of times what happens is that the DC solenoids do not have surge suppression on them. So when they are turned off the reverse voltage spike travels back up the line and starts destroying the weakest device on the line. In this case the Analog Output cards.
Transorb diodes or MOV's placed across the coil are very cheap insurance against this type of failure. DC coils are the worst, but AC coils should have surge suppression as well. I talk with people everyday that have destroyed a high dollar plc, touchscreen, or other piece of equipment from not using surge suppression.
Rajendrad,
A litlle while ago I also had kind of the same problem, what RRobin
is saying is certainly true but it also can be another thing.
Earthing, make sure that the earth of your plc is properly
connected. Also be sure that one site of the powersupply is
earthed. It's a typical Siemens problem.
Best regards Rudi
I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in...
1,144
Hello Experts, I need your help about this issue of mine about my Siemens Analog Input Card SM331 having SF LED lit. I know this is system fault...
4,488
Hi, I've been reading the contents of the forum for a while and finally decided to ask a particular question related to a project I'm currently...
4,316
I am a student. I can program PLC using LAD language using digital IO. But, I want to program using analog IO also. We have analog IO module with...
2,069
Hello I've got a signal from a potmeter ranging from 3v to 8v and a feedback from an actuator ranging from 0 to 10v. Ive tried to set up a...
1,502