Siemens FB41 PID
Banker
Dec 2005
aarslev
82
Hi all.
I have problem starting up a mixing plant.
There is 4 PID loops in the control system.
PID for: Flow Working range 0-30000 kg/h by a gear pump
Flow Working range 0-12000 kg/h by a gear pump
level Working range 0-100 %
Temp. Working range 0-250 C.
All the loops are very simpel i can control them i man. mode
but in auto mode only the Level loop can be controlled and even this loop is sometime not working. It is stable but 10 % from its setpoint.
I can adjust PID from a SCADA system.
I have the PLC program and can see the loops in the PLC (S315)
All the loops are scanned every scan and not i OB35.
The company that have make the program claims that it works in all there other installations.
My question is can i copy the FB where the PID FB is included
into OB 35 when the FB also controlling som start and stop.
Banker:confused:
If you can control them in manual mode and not in automatic, that means either gains are not set correctly, or something is connected wrong or scaled wrong.
FB41 must be in cyclic OB such as OB35 otherwise integral and derivative time constants don't have any sense.
Firt thing you need to do is to place PID controllers in OB35.
Second, you need to make sure you used correct units when using FB 41 inputs.
Good luck
P.S. Of course, if you have four loops you'll have four PID FBs and also four instance DBs
hello, I'm new in automatics, and i'm working on a speed control project for a hydraulic turbine. i'm using FB41 pid bloc, but the LMN give me 0...
2,265
Hi everybody, I am searching for some advices regarding PID controller with FB41. My program is designed for online blending with 2-3 components...
3,459
Hello all, I am an electrical engineering student working on a senior design project with an industry sponsor. We are automating a burst test...
26
13,954
Hi, I use an S7-315 CPU Used the OB35 and placed the FB41 in it. The cycle time is on default (100ms) I have humidity measurement in g/kg...
4,208
Hello, I need to set up the following PID controller: K(1+1/(Tis)+Tds)=0.6(1+1/(8s)+2s) (s-domain) in Step 7 project using PID FB41. I set up...
9,493