Siemens FM352 cam controller vs S7-1500 I/O
samvivi7
Apr 2016
NJ
50
Hey Guys,
need help comparing Siemens FM 352 cam controller with S7-1500 input and output cards.
- Do i look for the input/output speeds ??
- cycling speed?
i am really confused....
the cam controller has a lot of info regarding times for example, 5V input -24V output speed 1-4 microseconds, 24V input to 24V output 1-6 microseconds.
how should go about this??
Thanks for the help.
Sam
They can
Experiment, in Portal setup a technology object with a digital output module
But I think the best performance is the TM module
thanks,
also, i would like to do a hardware comparison;
The S7-1500 I/O
Input delay (for rated value of input voltage)
for standard inputs
— parameterizable Yes; 0.05 / 0.1 / 0.4 / 1.6 / 3.2 / 12.8 / 20 ms
— at "0" to "1", min. 0.05*ms
— at "0" to "1", max. 20*ms
— at "1" to "0", min. 0.05*ms
— at "1" to "0", max. 20*ms
VS
TM Timer DIDQ;
● Minimum pulse width for program reactions 3 µs for parameterization "none"
is this a correct comparison??
If I have a FM352 camcard that triggers hardware interrupts on camtracks, and a new hardware interrupt from a camtrack is triggered while OB40 is...