Siemens OP277 to AB SLC504 via DF1 and RS232/RS422 converter.
JesperMP
Feb 2003
ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
16,324
Hi all.
I am having trouble getting a Siemens OP277 and an AB SLC504 to talk to each other via DF1.
The older panels OP25/OP27/OP270 had an RS232 port and always worked OK.
Now the newer panel OP277 only has an RS422/RS485 port, and there must be a converter to allow it to connect via RS232 to the SLC504's Ch0 port. To this end I have installed the adapter 6AV6671-XE00-0AX0.
What works:
Downloading from the PC (WinCC Flexible) to the OP277 via the adapter and a null-modem cable.
Downloading from the PC (RSLogix) to the SLC504 via the same null-modem cable.
Converting the OP277 program to a PC RT and connecting to the SLC504 via the same null-modem cable also works OK.
What does not work:
Connecting the OP277 and the SLC504 via the same adapter and same null-modem cable.
The online settings have been checked. The program for the OP277 is a converted OP25 program that has worked before.
The dipswitches on the rear of the OP277 are set to RS422/RS485.
I have rebooted both OP277 and SLC504.
All to no avail.
:cry:
Solved !! Yahuuu :p.
It turns out, if you have the serial port on the panel enabled for transfer of the project - it disables the port to be used for the DF1 protocol.
Thanks to all that helped in the process ! ;)
Read something on another thread about Siemens 10 year support etc etc etc. Plant has been here for 6 years. Since I'm likely to be the one...
1,573
Hi, We have a project to upgrade old Siemens OP27 to OP277. In the OP27, we have production data (data record) and would like to transfer/copy...
4,469
Hi, I have a scenario where a customer has one spare OP277 to backup two applications, both applications using OP277's. Is it possible to...
6,212
188
145