Siemens S7-200 224 cpu
bill4261
Jan 2005
mid-west
99
How long does the 224 hold its memory. I guess I could look on Siemens web site, but I don't have 3 days to spare. I guessing it's slightly longer that 2 days. I have many of these in the field and only one customer that is having a problem. He has been turning power off to the machine for extended periods of time.
Bill
A supercapacitor retains the memory for a few days(4-5 if I remember correctly)
An additinal battery will retain the mememory for about 6 months.
If set to retentive, MB0 - MB13 are saved to EEPROM when the system powers down.
Another options is to save values, entered setpoints for example, to EEPROM by software, see SMB31 and SMW32
Thanks. I did find the battery backup on siemens web site. I need to find out how many customer issues we have before I change the code.
Thanks again
I vaguely remember reading somewhere that the supercap can retain retentive data for 100 days, If you are more concerned about losing retentive data then add an eprom module and use the program to write any retentive data to the eeprom that way if (assuming the user can change parameters like times/counter values etc) a value gets changed the new value is written to the eeprom and when a loss of retentive data occurs the new changed value will still be recalled along with the program/data block(s) etc.
Hello All, I am using siemens s7 200, CPU 224N. The problem is PLC has program but when i am uploading it, everything goes successful but the...
4,043
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
283
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
148
Hi, I have a 1214 on ip 192.168.0.100. This is connected to other modules through a switch on same network. I need to connect this to a company...
193
Hi Experts, I would like to make firmware upgrade from v3.0 to v4.5 (S7-1200 CPU 1215C). Can I do it from v3.0 to v4.5? Do I need to take some...