Hello,

I have understanding of AB PLC but I am new to Siemens PLC.

In one of the project, I have to go for Siemens SIL-3 hardware that too with fail safe I/O.

My question is, For digital Input module, do I need to wire single input to two channels?
e.g. for emergency stop with 2 NC contact, to wire in 24 ch fail safe DI module, is it necessary to wire 1 NC contact to ch:0 and other contact to ch: 11 ?

Please help me to get basic underandings for SIl-3 siemens configurations.
 
Hi,

I don't think this is very easy to explain. I would suggest talking to a Siemens rep who could help you choosing the right hardware.

The 400H is in itself not fail safe. The H designates it is High Availability (fault tolerant), you should look at 400HF or 400F. Or even 300F, since the 400 systems are very expensive.

And yes, you should have redundant channels. But to achieve SIL-3 there are more prerequisites..

Here more information:
https://support.automation.siemens....lib.csFetch&nodeid=6359901&forcedownload=true
 

Similar Topics

Hi What stage of its life cycle, S7-300/400 controllers are at now? In my existing unit, we are using these controller and in near futher there is...
Replies
8
Views
7,103
Hey guys, I've searched a lot to find the S7 PLC operating system but I couldn't find anything. Can anybody help me on this? and any helpful...
Replies
12
Views
15,986
Hi Folks, Was wondering if anyone can offer a bit of guidance. I tried downloading to a 414-2 the other day but was stopped due to lack of...
Replies
2
Views
3,296
I'm trying to get a handle on what is "Load Memory". Can any one explain what Load Memory is and how it is implemented?
Replies
13
Views
13,604
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
Replies
15
Views
344
Back
Top Bottom