Siemens S7-400 Cpu Slot Position
jimdi4
Aug 2004
108
Hello Siemens experts,
I need to know what slot position do I install my 6es7-416-2xk02-0ab0 CPU.
When I checked on the Siemens web site there were no manuals available for this CPU.
I have a 6ES7-405-0KA01-0AA0 Power supply in slot one.
I don't know if this power suplly occupies two slot spaces or not. Or the CPU occupies two slot spaces or not.
I also have to install an Industrial Ethernet 6GK7-443-1EX11-0XE0. I beleive that is supposed ot go into slot 4. So then I can start installing my Digital Input modules in slot 5 Correct??? :(
Jimdi4
A 416-2 will occupy 1 slot, your power supply will occupy 2 slots, so the power supply will take slots 1 and 2, your CPU will occupy slot 3, your CP443-1 will occupy slot 4, that leaves you 5 slots (in a 9 slot rack) for the rest of your cards.
Hope this helps
Paul
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,506
We are starting a project using a Siemens S7-400 CPU and must write data to a SQL server. We are also running a WinCC Server. Can the WinCC server...
3,244
Dear friends i am learning about stl so i need to know about the artitechture of s7 400 cpu i want to know how many registers and how they call...
3,188
I'm trying to get a handle on what is "Load Memory". Can any one explain what Load Memory is and how it is implemented?
13,587
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
330