Dont know if anyone can help,
We have the stated processor and all of the LED's on the front are flashing, but in a particular order, as follows:
All Off,
Then Batt F on for 1 second
Then All on for 1 second
Then All off except DC5V & Stop
Then All off.
We have tried replacing the processor, but the new one does the same thing and we cant even connect to it now, either through the Profibus network or directly via the laptop.
From the Simatic Step 7 software, we can get the station hardware config up, and it seems the only thing in there is this processor. Everything else is gone.
Nobody here is particularly good at Siemens S7, we are more AB trained.
Thanks for any help.
Mike
If there is a memory card in the CPU, remove it. Install only the CPU and the power supply. Make two consecutive memory resets. Then try to read out the message buffer via Step 7. Perhaps you find something that helps.
Good luck!!
All sorted,
It was the 24V power supply, running low at 18V. Changed that out and away we went.
Even Siemens couldn't tell us that!!!
Anyway, cheers for your help.
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
1,943
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
2,408
Hi guys, looking for some advice from someone with some siemens hardware experience. Im a student considering buying a siemens plc to practice...
5,050
does anyone why the cpu would go into stop mode as soon as the cp 343-1 lean is connected ?
3,284
i have a problem in communication between Danfoss FCM 1.5kW drive & siemens cpu 314 . I have assigned bus address as " 2 "in the drive ...