danfoss FCM gear drive communication with siemens cpu 314
rohanlyn
Aug 2011
uae
i have a problem in communication between Danfoss FCM 1.5kW drive & siemens cpu 314 .
I have assigned bus address as " 2 "in the drive . still not communicating . Can any one help in solving this problem
FYI
Ad Profibus node adresses:
0 and 1 is reserved for PG and OP
2 is default for a Siemens CPU DP master.
3 is a common default for a slave unit.
Duplicate adresses will mess up the bus completely.
Ergo est; You should number your slaves from 4 and upwards.
Kalle
danfoss FCM drive communication with siemens cpu 314
Thanks a lot . the problem was solved
There was error BF and SF on cpu 314 .
FCM drive was not communicating with plc .
Station address assigned as 2 and bus address as 1 - which is correct . but still not communicating .
Actually there was miss assigned profibus network . I assigned it as profibus DP and type as ppo type 5
At last this problem solved . Thanks a lot for your feedback
Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
56
Hi all, We are currently experiencing an DC over voltage fault on one of our inverters. During commissioning a snag was raised whereby excess...
224
hey guys i've been trying to find an updated SW files of my danfoss fc360 for MCT 10 software but i couldnt be able to find it anywhere on...
262
Hello all. I am hoping someone here has installed a Danfoss VLT Midi FC 280 and connected an encoder to it. I am just trying to make sure I select...
474
Good morning! I'm trying to communicate a Micro 850 (2080-LC50-AWB) with a Danfoss FC202 by VLT 121 MCA Ehternet ip card. I can read the value...
461