Siemens S7200 and Modbus RTU

micky

Lifetime Supporting Member
Join Date
Aug 2003
Location
DeRidder, La
Posts
83
I've got a CPU226 talking via modbus serially then converted to ethernet and being displayed in wonderware. My question is how do read/write bits say like M0.1? I can read the I's and Q's find but I dont understand how to link the modbus address with internal bits in the CPU226.
 
Without more info there's no way we can help you out. How do you communicate over modbus with the S7-226? There isn't a native modbus driver for the S7-226, you must have found it here or there or you must have written it yourself, based on info found out somewhere. It all depends on how the translation of S7-22X addresses to modbus addresses is done.

Kind regards,
 
I think you can read V-memory only, not M.
That's correct. But since there is much more V-memory than M-memory, it should be fairly easy to copy the M-memory to V-memory in order to make it possible to read out the M-memory.

Kind regards,
 
That's correct. But since there is much more V-memory than M-memory, it should be fairly easy to copy the M-memory to V-memory in order to make it possible to read out the M-memory.
i have used s7-200 224x cpu as RTU i have update all data to scada that is in single integer but now i have to show data of double integer using counter library vd to scada just want confirmation will double integer update on scada or not
 

Similar Topics

hey guys here first time for me in this awesome forum actually i have S7-200 connected to Winview HMI and HMI project file has lost and broken...
Replies
0
Views
605
Hi everyone I hope someone would be so kind to help me with this issue, I have trouble finding the way to declare a value which I want to be my...
Replies
1
Views
1,290
Hi everyone Does anybody know if it's possible to connect a termopar to an analog input directly? being more specific Siemens S7-200 analog input...
Replies
2
Views
1,690
Hello everyone, I am quite new both in this forum and in the PLC area. I am happy I found this great forum and hope one day I can help with my...
Replies
3
Views
2,244
I am trying to Configure Siemens S7200 (cpu222) with Vijeo citect scada on PPI cable but the problem i face in vijeo citect is that i am not able...
Replies
0
Views
4,312
Back
Top Bottom