Hey All,
I have a stupid question and need some help wiring the safety I/O (6ES7526-1Bh00-AB0). Attached-2 is what i think how E-stops and safety doors should be wired. Also for the safety doors can i wire only the safety outputs (1)??
(attachment -1 is for reference)
Thanks for all the help,
Sam
One thing to watch out for!
I'm not sure if it applies to all safety modules or just the ET200 safety modules, but I got bitten once and will never forget it.
Each input has a pair, and it's not the next sequential input. So if you have an e/stop and wire the first input into CH0, the other channel MUST go into it's respective input, which will NOT be CH1. On the 8-ch modules I was using, you had to wire them this way:
Input 0 and Input 4
Input 1 and Input 5
Input 2 and Input 6
Input 3 and Input 7
This doesn't help you with your immediate question, but it might save you having to re-wire half a panel like I did
Hello, I’m trying to get an understanding of safety PLC function, specifically Siemens. So far, what I understand is this: The user-programmed...
9,243
Hi Guys, My Name is Birdjie, I work for Moore Process Controls in South Africa. We encountered a problem with one of our FPSO Projects whilst...
2,459
My boss insists that we use a Siemans 300 series Safety plc for the application of counting and timing pulses at 15 hz 50ms width using 317F-2 CPU...
4,569
BACKGROUND We have been having a problem with unexpected stoppages of PLC recently. Another Contractor has possible tracked down the source of our...
4,383
Have never used a safety PLC (like S7 CPU 416F) What are the differences of programming between a safety PLC & a normal PLC? Could somebody give...
15,845