Siemens Simatic PCS7 Newbie Needs Help
wnelson72
Mar 2006
North Carolina
DOos anyone have a link for documentaion that can help a newbie understand how to incorporate field devices such as flow control valves (Fischer) and profibus based flow meters (E&H Promass 80) useing the Simantic Manager softare for Simantic PCS7. We have a S7-400 based systems .
I have no idea where to start. Electricians have wired instruments in field to PLC cabinets to certain slots. I can probably figure it out if someone just gives me a boost in trms of where to start.
Thanks in advance.
So... are you saying you have an S7-400 System... and no manuals?
Call your vendor and order at least one set of hard-copy.
Meanwhile, have you tried to log in on Siemens?
I know... the Siemens site really sucks... but you can, eventually, get to the PLC Manuals.
Setup your hardware first.
1 - Open the Hardware config in Manager.
2 - Get the GSD files for the devices you have. This is a text file that will tell Manager how to talk to your devices. They should come with them but you may be able to download them from the mfg web site.
3 - Import the GSD files for all your devices in your hardware config. This will only add them to your selections but not your project.
4 - Find your new devices and add them to your project. You will have to assign them a profibus address. Make sure the devices match what you show in software. They may have dip switches to set.
5 - When you drop the devices into your hardware config they should be assigned address.
6 - Download to plc and see what you get. From looking at the manuals of the devices and the address information in your hardware config you should be able to see how to use the device in your program.
Hope this helps.
Good Evening , It has been several years since I used Siemens Software . I’m looking to purchase the software for a Siemens Simatic S7...
513
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
563
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,079
Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
1,279
Hi all, First time posting here. I have a Siemens Simatic S7-1200 controller that I intend to use for a small project at home. I also have a...
2,056