Siemens Simatic S7-300 Question

arocon

Member
Join Date
Oct 2006
Location
Dubai
Posts
171
Could anyone please tell me why i am getting 'illegal command' message whenever i tried to download to the PLC and i can not download to the PLC. I use Siemens Simatic S7 CPU 319F-3 PN/DP. I am trying to use this function for taking data to the data acquistion system.

If anybody please help me as soon as as possible it will be great help.

arocon
 
You have transfers to QW3000 etc in your FC - have you/can you set the process image to cover these addresses ?

If not, then use PQW3000/PIW3000 etc.
 