SIEMENS SIMATIC S7 R system
naishadgosai
Aug 2005
surat,gujarat
39
Hello all,
I want a manual on SIMATIC S7 R (software redundency) system.
it will be more helpful if it contains comaprison between R & H (Hot redudndent) systems.
Hello naishadgosai;
Software redundancy manual (SWR_e.pdf) can be found here:
http://support.automation.siemens.com/WW/view/en/1137637
This can be setup on S7-300 and lower-end S7-400 PLCs, using MPI or Profibus channels to link the redundant processors. I/Os are accessed through a redundant Profibus-link, different from the one linking the PLCs (if this is the implementation chosen). Switch-over time is limited by the bus used, and the power/memory of the PLCs selected.
Hardware redundancy in Siemens world is called Fault-tolerant systems. Only the S7-417H and the S7-414-H can be used for this, they require a split central rack, redundant power supplies and special fiber-optic connections to link the redundant PLCs; communications with I/Os is over redundant Profibus-DP (using a Y-Linkl and ET-200M). Switch-over is extremely fast, and memory integrity is ensured by copyig the primary's memory to the stand-by at every cycle.
Here is a link to the basic manual for Fault-tolerant systems from Siemens:
http://support.automation.siemens.com/WW/view/en/1186523
Hope this helps,
Daniel Chartier
I have a customer of mine who used Siemens Simatic S5 software it is the version that still runs in DOS but I beleive it is newer then version 3...
3,556
Good Evening , It has been several years since I used Siemens Software . I’m looking to purchase the software for a Siemens Simatic S7...
507
I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
558
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,075
Hi. I have 2 files where I would like to see the ladder logic differences (similar to the Rockwell compare function). I am using TISoft Siemens...
1,274