Siemens System Layout
rahilansari
Jul 2008
INDIA
103
Hi All
I have designed a Siemens system(please see attached).The system can be described as follows.
1.The system is a Pumping Station and has 5 RTU units.
2.Hot standby redundancy is required for main pumping station.
3.Fibre optic should be used a communication medium between RTUs and Main pumping station.
4.Pumping Station Communication network i.e., PLC to SCADA and PC to PC should be redundant.
So can you please check the layout and tell me whether it is workable or NOT(From hardware point of view)..
Rahil
As your system is designed now, the switch "in the middle" can bring the whole thing down.
I think you can make a copper ring between the PLCs and the copper/fiber switches. That gives you some redundancy at this level.
Dear Jesper
thanks for your reply.
I want to use Intel Teaming card for communication between ES/Servers and OS clients in Terminal bus.
Does Siemens itself supply this card if yes,Will you please tell me the part number since I am trying it in catalog but didn't found anything.
Hi all, This is going to be a long post apologies. I'm also a complete beginner to the world of PLCs. I'm currently working on my first ever...
457
Respected Members; We are going to design F&G System. The third party quote following 1. CPU S7-1200 1214FC, 2. Analog Input Module SM1231 3...
2,076
I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were...
1,896
Hello All, For S7-400H system, can we make this redundant PLC (connected to one uplink switch) to communicate simultaneously with 3rd party HMI...
1,472
Friends, As someone who has spent several years troubleshooting Control Logix PLCs, Factory Talk View, Powerflex drives, servo drives and...
3,410