Siemens TD200 Alarm Display

danmottram

Member
Join Date
Feb 2011
Location
wirral
Posts
1
Im using a TD200 with a S7-200 PLC.

I have configured the alarms, and i have set it to default to operator/user screens not alarms at the request of the customer. However is there a way to make the alarm screen appear when there is an active alarm? or is there a way to configure one of the buttons to take you to alarms instead of using the ESC key and navigating the menu?
 
Hi!
There are three ways to display alarms:
1. Configured alarms: Notice that each alarm has a dedicated (wizard generated) control bit. Use those bits to display alarm.
2. Do not configure alarms, write alarm messages in normal screens. So in case of alarm, just display a proper screen by changing VB byte which control the screen displayed.
3. Put a s string on one screen. Make some predefined alarms strings. In case of alarm copy (using indirect addressing) desired string to a string displayed on the screen.

Best regards!
 

Similar Topics

Beause Siemens TD200 has been discontinued,I still need to use some of the machinery.I nedd td200 alternatives.Can anyone tell me what the product...
Replies
0
Views
2,318
Hey, I have a TD200 and an S7 200 connected. I set up the TD with the wizard - parameter block starting at VB0. Only have 1 message - enable bit...
Replies
0
Views
1,595
I have an S7 200 plc working on a machine. it's TD200 display is damaged. Now I have purchased a new one. do I have to program it or just install it?
Replies
4
Views
2,388
Hello everybody I have system which include S7 200 and TD200 V3 I need to let the operator to change 2 values VW0 and VW2. I follow the wizard...
Replies
3
Views
8,823
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
2
Views
97
Back
Top Bottom