First of all i wish to thank you to
@sps-concept for his help .
He knows Interbus together with S5 , and he knew it from the beginning that Interbus it's stored in DB10 - DB13 .
He have tould me, the Interbus network reconfiguration must make it from Step5 , and not with Phoenix Contact IBS CMD SWT G4 software .
Then i must to thank you for
@sigmadelta and
@KalleOlsen , because he have advice it here to delete OB19 , OB23 and OB24 .
I've delete it this blocks, and then i've read it the I-stack and B-stack .
Attached you can see it what I-stack and B-stack show it to me .
@sps-concept have modified the PB 100 segment 2 :
PB 100 Segment 2
instead :
JU FB 100
he have write it this :
A F 0.0
JC FB 100
And after this the
Interbus have gone it in
RUN ,
PLC have gone it in
RUN .
===========================================
@sps-concept have tould me many many times , to not search anymore Interbus communication erros . When the Interbus it's in RUN , PLC it's in RUN , i must to concentrate about missing Inputs .
But the question is : If FB 100 was "jumped" , i'll not need the FB 100 in other side of PLC software ?
So , to "jump" the FB 100 it's a good solution ? I will not need this FB 100 block in other places in PLC software ?
I know the PLC and Interbus it's in RUN in this way , but i can make to work the machine with "jump" of FB 100 ?
Or i'll need it somewhere else in PLC software, and i'll can't use it, because i've jumped .
===================================
@sps-concept have experience with Interbus , and until now everything what he said about Interbus was a good decision to trust him .
I have an operator panel Sutron BT20 , which communicate through Interbus with PLC .
But right now, the F1 - F9 buttons from BT20 panel doesn't work it , and i don't know it why .
The BT20 doesn't let me to enter values , the F1 - F9 button small led lights are inactive ( doesn't lighting ).
And every stored value in BT20 menu "Mask" it's : 0.00
That means the BT20 doesn't communicate correct (totally) with PLC S5 ?
The "Mask" Menu appears , but i can't enter any value , and the F1 - F9 buttons are inactive .