Simatic S5,375 Memory Submodule Flash Eprom, 8 Kbytes
Gromit
Jun 2006
119
Hi
I'll use this memory module with an S5-90U system:
6ES5375-8LA12
SIMATIC S5,375 MEMORY SUBMODULE
FLASH EPROM, 8 KBYTES
FOR PROGRAMMING
STEP 5 V6.6 NECESSARY
Is this memory module flash or eprom? I mean can I use it like the eeprom?
Can I delete and reprogram it electrically, many times?
Thanks in advance
From the siemens website:
S5: can you write the Flash EPROM 6ES5 375-8LA12 directly in the AG90?
QUESTION:
Can you write the Flash EPROM 6ES5 375-8LA12 from the AG90 like an EEPROM?
ANSWER:
No. Reasons:
  1. The module replaces with full compatibility an EPROM module, and therefore also the EPROM module ID in MLFB and the module hardware.
  2. Due to its firmware the PLC can only write modules with EEPROM ID.
  3. In order to write modules you need a driver (supplied as of PG/PC software STEP5 V6.6) that is not implemented in the AG90 firmware and is also not planned to be.
I need information on Simatic S5 EPROM Memory submodule 8kx8bit 6ES5 375-1LA15. It is thanked for to him by its collaboration
6,235
We are facing intermittent issue with emergency stop and line stop. Line stop triggering with alarm of line stop push button activated at one...
216
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
108
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
188
Hi, I received this SIMATIC S7-300 training kit for maintenance. When I power it up, the PLC doesn't go to RUN mode and the STOP mode led is...
323