Simatic S7 Question

arocon

Member
Join Date
Oct 2006
Location
Dubai
Posts
171
I attached the network. I have 2 questions about the network:

1) How to Reset_Position make 0.
2)How to force a value to the 'EN_PSH1_APTR1.IWD1','EN_PSH1_APTR1.IWD2', EN_PSH1_APTR1.IWD3',EN_PSH1_APTR1.IWD4'.


If anybody please reply me it will be great help.

Thanks

encoder.jpg
 
Looking at your image, it looks like Reset_Position is already being loaded with a '0'.

To force a value into the words you could use the Variable Table (under the menu PLC -> Monitor/Modify Values.)
 
If nothing is writing to the variables, you can modify their values within the same screen as your screenshot, by simply going online > Right click > Modify.
Or by creating a VAT (Variable Table).

If some part of your application writes to it, then you need to either stop that or use temp variables for testing purposes.
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
83
Hi, first post here so sorry for it being a noob question but what can I do .. I need help (and of course I need it yesterday :banghead: ) The...
Replies
11
Views
5,910
Hey all. I've got a query for you. Does it require more of the processor of a PLC to generate the time value everytime a timer is called upon...
Replies
8
Views
1,422
Could anyone tell me when Network 9 will be enable ? or when value of OUTV will change ? Thank you
Replies
1
Views
1,805
In one network SFC20(BLkMOV) is used to transfer 8 byte data from P#DB500.DBX8.0(SRC BLK) to P#DB20.DBX4.0(DST BLK). I would like to change...
Replies
2
Views
4,280
Back
Top Bottom