simple photo eye problems!
bigrthanur
Mar 2007
Ohio
85
Wow today i am having a big problem and felling pretty dumb! I am trying to use a banner vs1 photoeye as an imput into my slc 500. You can wire it up using pnp and npn but i can not get it to work npn(pos. switching) For anything! I have 3 wires blue, brown, and black. The black wire on the print is showing load and i am using it as my signal.
I can get it to work as neg. switching(but dont want to use a relay), but not pos. switching. What kind of a load do i need on this thing?
Thanks!
I am not familiar with this type of photoeye but with photoeyes i've used before there has been a switch on the photoeye to choose npn or pnp.
Just change the logic from XIO to XIC or vice versa......In the old days of relay logic this was a problem PLCs make it easy. :site:
On this particular model you ONLY have NPN switching mode.
Usually 4 wire sensors have the switch or by selecting the wire (Black or white) you select your switching mode (PNP or NPN).
If you do not want to purchase a new sensor and your application (detection time) isn't a fast one, use an optocoupler to do the NPN switching for you so you can interface it to the existing PLC.
PNP/NPN is not the same as normally open/normally closed.
PNP and NPN devices can both function as normally open or nomrally closed switches.
A PNP device applies a voltage potential to an input terminal.
An NPN device is connected to an input terminal which sources a voltage potential and swtiches that potential to ground or neutral.
PNP_sensor PLC
+24VDC--------] [-------------[Input]----0VDC
PLC NPN_sensor
+24VDC------[INPUT]--------------] [-----0VDC
However, an NPN device could be wired to sink the voltage applied at an input and then the logic would be inverted with respect to the PLC input, which may be what you were thinking, there is just more to it than software logic. It must be wired differently and an upstream load must limit the current.
CURRENT_LIMITING_LOAD PLC
+24VDC----/\/\/----------+-------[INPUT]-----0VDC
| NPN_SENSOR
+---------] [-------0VDC
In this instance, the PLC input sees voltage potential when the NPN sensor is OFF.
A better solution is to match the PLC input type and the sensor type, even if that means buying another sensor, ie, the correct sensor.
I agree with Alaric. It's not really a question about PNP or NPN sensors.
I think it may be more of a question on light operated or dark operated photoeye modes.
I prefer dark operated mode photoeyes in case a wire gets cut I'd rather have the input default to being blocked than clear in most situations.
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
170
Hi all, Writng a FB in ST on Beckhoff TC for a pulser which turns on and off on a cycle, is paused by turning bControlInput to FALSE, but resumes...
258
I'm trying to build my Classic Step 7 programming skills this weekend. I get stuck on little things that are not covered in YouTube tutorials. I'm...
319
I have a program that does a 7 second "scan" sensor calibration routine whenever a setting (setting is called assistance level or "AL" and ranges...
214
Hi all, I have a simple question that I have overcomplicated and gotten stuck on. I have a variable, we can call it "light" that I need to stay...
321