Sinamics S110 STO ramp?
Pete.S.
Mar 2016
Fl
463
I have a system with a S110 and a servo motor.
When the operator hits the emergency stops the STO function in the S110 is activated. But it seem to stop too fast and it causes mechanical problems.
Where can I change the ramp the S110 uses to stop when emergency braking?
Thanks,
Pete
If the operator is hitting E-Stop when it's not an emergency, it's time to either retrain the operator or redesign the control system. Emergency stop should be to stop as fast as possible and not part of the normal operation of the machine.
Pete
Interesting because STO is safe torque off (coast)
You sure your not using SS1 which has a time ramp?
Go online with the safety integrated part of Starter and do a screenshot
Btw
I agree with Steve
If my arm is in the machine, I don't care what happens to the machine as long as it stops :)
Thanks Steve for your concern. This is not one of those cases though.
Machine should also stop as safely as possible, not always as fast as possible. Basically it's a matter of risk assessment, check ISO 13849-1.
For instance imagine a metal lathe. If you stop as fast as possible with a servo motor, things will come flying out of the chuck. That is not safe for the operator.
Pete
Btw
I agree with Steve
It's STO for sure.
Are you sure it's always set to coast or can this be changed? I can't find any settings for this.
Regular VFDs coast but this is a servo controller after all. But maybe that makes no difference - I'm not sure.
Look in to using SS1. If I remember correctly when SS1 is used then quick stop ramp is enabled, after that time expires then STO.
Check the manual. I don't have timing diagrams in front of me
But you should be able to accomplish your goals
Of course! šŸ™ƒ
STO have to disconnect everything electronically so it have to result in the drive coasting to a stop. So this is a category 0 stop. And of course I can't find any settings for a stop ramp because there can't be one.
I took a look in the manuals and SS1 is a category 1 stop as you say. Since I can't stop the drive too fast, it's of course a category 1 stop I need to do.
Thanks a lot!
interesting thread, I too was having the same problem
Dear All I have Sinamics S110 drive that I will use to control a conveyor belt in steps, I have a 10 meter long conveyor belt, on the belt I have...
1,121
Dear Gents First a happy new year to all šŸ» I am playing around with a S110_CU305_PN controller and is trying to make it as automated as...
1,527
Sir, At present i can write one parameter at a time, but how to write multiple parameter in sinamics s110 using SFC 58 in S7-300. And also...
2,384
Hi dear, I'm totaly new in S110 SINAMICS.. i have a question about S110 sinamics. Normaly u have a function block to read your position about...
2,286
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
101