single ended versus differetial AI
RY_Guthrie
Nov 2011
Las vegas, NV
263
I am trying to find a simple explanation of the difference between single ended and differential analog inputs. I have read over the Rockwell manual on the analog input module but it really doesn't give a good explanation on how and why I would use either.
May be this can help:
Analog input interfaces can receive either single-ended or differential inputs. The commons in single-ended inputs are electrically tied together, whereas differential inputs have individual return or common lines for each channel. Single-ended modules offer more points per module than their differential counterparts. Depending on the manufacturer, a module may be set to either single-ended or differential mode during software setup using rocker switches.
one other point is that differential signals offer a higher noise immunity than single ended due to the isolation of wiring.
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um009_-en-p.pdf In the above 1756-IF16 document on page 43, it...
4,993
I actually don't understand which device determines whether the wiring will be single ended vs differential. being single ended or differential...
3,188
Dear Experts, Is it allowed to use 4 wire sensor 4-20 ma (external power loop) with control logix analog card ( 1756-IF16 )with a single...
3,040
Hello, I have a 1756-IF16 configured for single-ended current inputs. I plan to add (4) 4-wire density transmitters. The operating manual for...
2,424
If I am using an 1756-IF16 analog input module, single ended do I have to jumper all iRTN and RTN as shown in the wiring diagram. I have a mixture...
3,618