I want to be able to connect an Allen-Bradley slc5/02 processor to an ethernet network. I found the prosoft mv146-dfnt module would accomplish this. Are there any other modules that would work, or is the mv146-dfnt the only one? Bryan81
I have considered changing to a 5/05 processor, however I do have rack space and the prosoft module is more cost effective than the 5/05. I am wondering if there are any other addon cards that would be better and/or most cost effective.
Bryan,
Don't overlook the cost of programming with the DFNT. I've used one before and you have to map all your data points to the registers that the DFNT will recognize, all through ladder. The cost difference between the DFNT and the 5/05 may be close to a wash when you figure this in.
HTH,
Jeff
Here's something unusual: I'm going to mention an architecture that *won't* work.
Although on paper the 1761-NET-ENI is an EtherNet/IP to DF1 bridge, and the 1747-KE is a DF1 to DH485 bridge, connecting the two together in practice does not result in a full-featured EtherNet/IP to DH485 bridge.
I connected just such a system in my office to check it out. I was able to browse in RSLinx far enough to "see" the controller in the RSWho window, but could not go online, upload, or download. Only the controller at Node 1 could be accessed.
I was able to successfully poll data from the controller using RSLinx Professional and Excel, so I know that messages can get through this link. But the messages necessary for upload/download/online monitoring will not.
If this installation is only for monitoring of the SLC controller by a PC, you could use a 1747-KE along with an off-the-shelf Ethernet/RS232 converter like a LanTronix, Digi, or Moxa converter. These emulate a Windows COM port so Windows programs can use them.
Again, if you want fast online monitoring and programming of a SLC controller, the best way to go is to get one with Ethernet built in, i.e. an SLC-5/05 controller.
Bryan,
One other little thing I forgot about the DFNT, which Ken's post reminded me of, is that you can't program your 5/02 through it, i.e. no uploads, downloads, or going online via RSLogix. It's main use is to give you access to data points over ethernet. So even with the DFNT installed, you would still need to hook up your PIC or AIC to the 5/02 to program ladder that would allow the DFNT to expose data points. Kind of ironic.
Don't get me wrong, the DFNT served me very well and is a good piece of hardware, but as Ken said, if you are planning on programming over ethernet, your best bet is the 5/05.
Jeff
Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
436
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,654
We are replacing a piece of machinery with a newer version. The new assembly has 5 TCs which are closer by far to the operator station than the...
2,280
Will a PVP7 talk to an SLC 5/05. I can't get them to talk. I have set up PVPs to Control and Compact logix plenty of times, but can't get these to...
2,535
Hi all I have a legacy PLC (1747-L552C) and I have been asked to look at remote access (it's communicating via ethernet to a PVPlus6). I have an e...
1,546