The slot that you select for your SN module will determine the I/O addresses of the points in your remote chassis(s). Think of the SN module as a very large I/O module. That is how it appears to the processor.
Say you choose Slot 2. All RIO inputs for that scanner will be I:2/xxx. All outputs will be O:2/xxx. How the I/O is mapped to each slot in your remote chassis(s) will depend upon how you configure the ASB module. With single slot addressing selected, each slot will be assigned 16 bits. In that case, an 8 point output card in Slot 1 would be assigned O:2/00 through O:2/07 and an 8 point output card in Slot 2 would be assigned O:2/16 through O:2/23.
Analog I/O in an SLC remote chassis can be a PITA to work with. If you can, you'll save yourself some trouble by placing all of your analog I/O in Chassis 0, rather than in the remote I/O chassis(s).