SLC 5/05 with Panelview 1000 plus
srv
Aug 2010
QATAR
109
I am facing a problem with Panelview1000 plus programming.I came to know that we cann't give direct bit address to RS view ME like wonderware.Tags only we can import to ME.I had one SLC 5/05 and Panel view plus 1000,working properly.Unforunately I don't have development of that ME file.But i checked PLC programs by uploading from PLC,i could n't find any description or tags in PLC program.But it is working propery.I tried with another ME program which i did myself from my computer,but i couldn't communicate.anybody please tell me how i can import address from RS logix 500 and communicate to PLC
I came to know that we can't give direct bit address to RSView ME like Wonderware.
This is incorrect. You cannot use the FactoryTalk Tag Browser to directly select a bit in a data table word, but you can easily select the data table word and append ".xx" for the bit number.
This is only partially correct. You can import SLC or PLC data tables into FactoryTalk View HMI database tags, or you can use Direct References to the SLC or PLC data tables.
The principal function that is supported for ControlLogix but not for PLC/SLC is the direct reference browsing of an offline controller project file.
Online direct reference browsing is supported both for PLC/SLC and for ControlLogix.
I checked PLC programs by uploading from PLC, I couldn't find any description or tags in PLC program. But it is working propery.
This is because Symbols and Descriptions in all Rockwell Automation controllers are part of the RSLogix project file and are not stored in the controller itself. You must obtain the documented RSLogix project file in order to see the Data Table descriptions and the Rung Descriptions.
Anybody please tell me how I can import addresses from RSLogix 500 and communicate to PLC.
To learn the fundamentals of FactoryTalk View communications, I recommend the User Manuals as well as the RSLinx Enterprise "Getting Results" guide. These are installed along with FactoryTalk View Studio and can be launched from the Help menu.
They are also downloadable separately from the Rockwell Automation literature library.
FactoryTalk View Machine Edition User's Guide:
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/viewme-um004_-en-e.pdf
RSLinx Enterprise Getting Results Guide:
http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/lnxent-gr001_-en-e.pdf
Hello, I have been asked to update a really old system. It has a 1747-L542 (SLC 5/04 32KB) and a 2711-T10C8 (PANEL VIEW 1000). I have the...
1,672
Hi, What configuration needs to be done in RSLINX ENTERPRISE RUNTIME in order that panelview plus 1000 to talk with SLC 5/03 ? I tried to copy...
2,376
Hi, I can not make to communicate a SLC 5/04 with a Panelview Plus 1000. In Local Mode everything seems OK, but in Target ... I don't realize...
3,230
We have a system with a Panelview Component 1000 and an SLC 5/03 on the floor. Does anyone know if the Component screen can be connected directly...
2,755
Dear all, I have one Panelview 1000 HMI and one SLC 5/04 PLC. Both are Allen Bradley. Currently my Panelview 1000 HMI malfunctioned. So i need to...
6,106