SLC 505 L551 OS501 FRN11. CIP (ethernet) MSG-READ from 3 seperate Micrologics 1100 B .IP's are correct (the PV 1500 reads the F8:0 address from the micrologis with proper values), but the MSG instructions within the slc 500 timesout (error 37) . Did I mis-configure the Channel 1 settings of the micrologis?
target CPU = slc500 (is this correct for a MSG read to a micrologic 1100 B)
controlblock = N7:50
length = 51
Without seeing your code, it's tough to say why it timed out. If it read once, it should read everytime. How are you triggering the MSG? If this MSG the only one in your program?
When the target device is a MicroLogix 1100/1400 controller, make sure you are using the "Multi-Hop" option.
You might only have to enter the target address, or you might have to add another hop to "ControlLogix Slot 0".
Double-check the target IP address. RSLogix 500 enforces an old rule about leading zeroes designating octal addresses, so "192.168.1.10" and "192.168.1.010" are not the same.
i have a 505 and a micro 1100 on the same same network. how can i set an output on the 1100 when i have a bit to go high in the 5 05? thank you:hmmm:
1,586
HI, i am wondering if micro 830 using controlled components workbench has a way i can uttilize a TOF from an old slc 150? In addtion If I...
2,735
I, i'm trying to communicate with a Pv300 micro (2711-M3A18L1), via my Slc 5/04 rs232 channel, using DF1, and a home made, 1761-CBL-PM. The...
4,426
Hi all, Just trying to set up communications between an SLC5/03 and a Micrologix over a phone line and I am using two telephone modems. In the...
1,977
I'm thinking I need a newer version of software. I have 2.10.12. I have a SLC 5/05 ethernet processor. I don't have the original program, so I'm...
5,735