HI,

i am wondering if micro 830 using controlled components workbench has a way i can uttilize a TOF from an old slc 150?
In addtion If I understand correctly in slc150 RTO is a TON in 830 micro plc using ccw Finally short of having another slc 150 can I drag old program off e prom?

Thanks
Ron
 
Ron,

1. Yes, there is a TOF instruction available for the ML 830. Select a "block" from the toolbox and drag it onto your rung. Double click that block and select TOF from the list that pops up.

2. An RTO is different than a TON in that an RTO will retain its accumulated value when the rung goes false. A TON will reset when the rung goes false unless you add programming to make it function that way yourself. That said, you can download sample code from Rockwell that includes a user defined RTO instruction. See knowledgebase article #450811.

3. It has been a long time since I worked with an SLC-150, but I believe you'll need a controller to plug the EEPROM into to get the program out of it. You can then use a hand held programmer, and it will only display one instruction at a time. I would use it to draw the logic rungs by hand so you can see it all at once, and then write your new logic for the Micro 830. There was software and an interface converter for the SLC-150, but I never used it. Regardless, there is no conversion utility I am aware of.

Hope this helps.
 

Similar Topics

I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
978
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
Replies
9
Views
775
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
Replies
16
Views
1,367
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
565
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
Replies
0
Views
432
Back
Top Bottom