I have a Analog Input Class 3 module, 1746-NI8. When doing the configuration, specifically moving the analog configuration to the Output Words, do I have to set the word length to 12? Or can I keep it as eight (8) as in a Class 1 module?
Regards.
Word lenght is 12 for class three. The software will do this for you, automatically. If you are changing from class 1 to class 3 then delete
the instruction for the output configuration and let the software readd it for class 3 configuration.
I don't remember what AB has to say about it, but I have used both. It looks like if you use eight you wont get the channel status though.
Class 3 vs Class 1 just adds additional 4 words for setting user scaling. You can still have the module entered in the configuration as Class 3 and only write 8 words, as long as you don't configure it for user scaling. However, you will still have 12 words allocated in the Output image file for the module. If you really only want to use the 8 words, I would do as others have recommended, and remove the Class 3 and enter it as a Class 1 for the sake of consistency.
So i have a 1746-NT8 thermocouple for a conveyor furnace that is causing some problems. When the CPU is in run mode the channel 6 LED flashes, but...
1,613
Hello, We have an old SLC 500 that has two 1746-HS Single Axis Motion Control Modules. One of these modules is bad. Verified by swapping out a...
1,169
Hello, I have a few boards, the same, which are: 1746-OB16/D It seems hard to find the manual online. Any help with that please. My question...
1,278
Hi everyone.. I have 1 basic module SLC 500(1746 Bas), now i want to back up programmed (upload), but i dont know to cumunicate with this...
4,718
Hello all. I have an output module that I'm trying to wire-in and don't know if the module is bad or if the installer (me) has done something...
26
8,646