Slc 500- 1747 hsce wiring issue
sinanmoral
Apr 2020
Istanbul
52
Hello,
First I looked at Manuel and Plctalk but I did not find or maybe not understand.
How I can connect ''HTL / Push pull-24 volt encoder'' to the terminal of 1746-HSCE?
Encoder Model; DFV60B-22EZ0-S01- Sick..... (there are just 5 pins= 2 pins for Powers +Others A,B,Z)
Also, I see '' Ls,Com, Ls (5VDC),Ls(12 VDC) and Ls( 24vdc)'' on 1746-HSCE modul.
What is for them?
Can I connect '' A, B, Z pins of the encoder(HTL)'' to directly A, B, Z of 1746-HSCE?
The title is wrong and will be 1746 hsce
thanks in advance
JaxGTO,
Thank you for your answer but these dip switches are for output. Not for A,B,Z
Below copied from Manuel...
'' Dip Switch and Jumper
Locations
• SW2 selects the output voltage range (4.5-10V dc or 10-30V dc). ''
Any comment appreciated in advance.
Check page 3-2 about using pull-up resistors for using 24vdc encoders.
Single-Ended Encoder Wiring (Open Collector)
Or page 3-14 for
Single-Ended Wiring (Discrete Devices)
Be careful about connecting encoders to the HSCE, the inputs are typically 5v, some encoders will only work at higher voltages, there is a part in the manual what size resistors to fit should higher voltage encoders be fitted. do not get confused about LS & outputs as these can be configured at different voltages, I know someone who did not realise the voltage variations on some encoders cost them a couple of cards.
Dear All, I need to upload program from slc 500 fixed controller (1747-L40C), series "B" and FRN "6"and to download the program to another PLC...
23
7,262
Good Afternoon, I plan on replacing some SLC 500 PLC's with CompactLogix. Could you tell me what the equivalent processor is in the...
2,290
Having a problem with is processor PLC SLC 500 cat:1747-L541, the fault light is flasing and cannot go online and again the DH+ comm. is flushing...
1,793
Good Morning , I have a SLC 500 rack with a 1747-L542 CPU and 2 DeviceNet scanner cards. I am having a terrible time going online with this...
4,357
I have used SLC I/O on 1747-AENTR with SLC Chasis. Successfully configured All SLC I/Os along with 1747-AENTR. My question is what is the...
3,292