Setpoint (SP)
Input
Parameter
Descriptions
Address Data
Format
Range Type User Program
Access
SP - Setpoint Word 2 word (INT) 0 to
Parameter
Descriptions
Address Data
Format
Range Type User Program
Access
SP - Setpoint Word 2 word (INT) 0 to
16383
(1)
(1)
The range listed in the table is for when scaling is not enabled.
With scaling, the range is from minimum scaled
(SMIN) to maximum scaled (SMAX
control read/write
***I have an issue how to write to the Sp input of the PID instruction.
Listed above (1) The range listed in the table is for when scaling is not enabled.
1 So how can I enable the scaling???
(1) The range listed in the table is for when scaling is not enabled.
2 For say if my set point ranges from -328 to 1562. Do I have to Use the SCP SCALE WITH PARAMETERS intruction, and scale the sepoint than write the output of SCP to the
SP - Setpoint Word 2 word (INT) 0 to 16383 ?
3 With scaling, the range is from minimum scaled
(SMIN) to maximum scaled (SMAX)
So if my (SMIN) is -328 and (SMAX) is 1562.
Do i just move actual set point (lets say -150)to The PID control Block Word 2??
Thanks for all your help??