SLC Rack Connect to A control Logix plc
Donnchadh
Jun 2002
Ireland
1,004
Hi all
I am looking at a project ,and as part of it I have to remove
a slc 5/05 processor.The slc rack has two,eight channel analogue
input cards and the rest is digital in and output cards.
We are adding in a control logix so my question is,what is the best
way to tie into the slc rack.Is it by adding a DH+/RIO card in thr control logix and a SN card in the SLC rack.I have seen posts here
about PLC 5 and using the rack as a rack in the control logix program.Is this correct and is there a way to set it up as a devicenet rack as we have a devicenet scanner in the control logix.
Thanks for taking the time to read this.
Donnchadh K.
Depending on your available resources, the solution can come in many different forms...
1. Totally replace the SLC hardware with ControlLogix/FlexLogix/CompactLogix hardware.
2. Do the RIO thing. Remember the scan rate and communication rate of RIO.
3. Utilize the SLC5/05 processor as an IO handler.
4. ???
Why not leave the 505 and use ethernet to communicate with it, Instead of buying a DH card and a SN card - then your kind of regressing from ethernet to slow DH
That was my thought. It depends on bandwidth though.
If you want to use the SLC rack as remote I/O to the CLX processor, you will need a DHRIO card in the ControlLogix chassis, and a 1746-ASB (NOT a 1746-SN) in the SLC rack. This is crucial.
The 1746-SN card is a scanner or Remote IO master, where the ASB module is an adaptor. The ASB is used in the remote rack to connect to an RIO scanner.
Hi All
Thanks for the reply.I think I will go with leaving the processor
in and just map the I/O across ethernet.
Does anyone see anything wrong with this.
Thanks again
Donnchadh K.
Yes, there is (potentially) something wrong with that.
You will have to roll your own determinism to use the SLC ethernet channel without worrying about what might happen if I/O don't get updated for a few seconds or longer.
Be sure to carefully study the timeout periods, and/or add your own heartbeat logic to shut things down and test it by unplugging the cable.
The worst thing about your situation is that A/B still has not put forth the effort to write firmware for the 1746 controlnet adapter to make your hardware controllable via controlnet.
Apparently they have no intention of doing this or it would have happened by now. I am sure they are selling a lot of controllogix cards because of the poor choices they give us for controlling 1746 I/O with logix.
Be careful
Paul
OkiePC is correct. All you can do between a SLC 5/05 and a ControlLogix over Ethernet is messages. If you are using any 'critical' commands over this link you need to build in your own error checking (I vote for the heartbeat idea, by the way) and response. This would mean the SLC would need to be effectively free-standing as far as local functions are concerned. The ControlLogix would just issue very high-level commands.
What I would like to see in the 1746 family is to have Ethernet I/P slave firmware added to the SLC 5/05. Set it up like a PLC5 Remote I/O slave but over Ethernet. But I agree with OkiePC. Just like the ControlNet card, I doubt we will ever see it.
Keith
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
525
Is this possible to do on the SLC platform? The reason I ask is I would like to upgrade from a 5/04 to a 5/05 in one machine to get the use of...
1,727
HI guys, wondering if anyone has used a 1746-C9 rack extender cable to connect 2 (or more) SLC 5/05 racks when upgrading the SLC to compact logix...
3,269
All, Thanks for any help. I am currently changing out an 1747-L543 processor over to an 1747-AENTR card so that I can now run this rack from an...
2,112
Hi. I am trying to reproduce a customer issue with a multi rack SLC configuration. I have multiple SLC racks (2 4 slot racks with 1746-P2 power...
21
4,487