hi all1
i want to communicate and programme my slc 5/04 with panelview550 2711-b5a5,,
can any one guide how i communicate HMi with my slc5/04,,

and how i interface both to communicte each other(means how i declare protocols and adressing)?

thanks in adavance.
 
Your PV supports DH485 protocol. You will need to configure the serial port on your SLC5/04 to DH 485 protocol. You can then use a straight thru cable AB# 2711-NC13
or construct your own.

Pin 2 to 2
Pin 3 to 3
Pin 5 to 5

If you want to connect to both with a programming PC/Laptop then you will need a couple of 1761-NET-AIC ( see pdf below)
If your PC/Laptop does not have a real serial port then you will need a 1747-UIC ( USB to DH485 converter) to connect to your DH485 network.
 
Last edited:
Thanks MIckey...thats nice and seems easy! :)

but confiquration Dh485 protocols ??this confuse me,,,some literature or guide how protocols are declare and adressing pv?
 
You configure the SLC's serial port thru RSLogix500.
Under "Channel Configuration" See picture below.

Configure the PV's port for the same baud rate as the SLC and a different node address Using Panelbuilder32 software. Or thru the PV's configuration screen.

Be advised once you change to DH485 protocol you will need some hardware to reconnect to the SLC' serial port, the above mention 1747-UIC. Or a 1784-U2DHP (USB to DH+ converter) to connect to its DH+ port

See links below for the hardware and instruction set manuals.

https://www.google.com/url?sa=t&rct...QdfKe4bVcp3gKfYbQ&sig2=Nh9eyr_u6jWtegowFp-MeQ

https://www.google.com/url?sa=t&rct...gvlYXCAHbB1Dd61SA&sig2=vDcIt4S9nvWLfgAqBNgGoA

channel0config.png
 
Last edited:

Similar Topics

Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
639
I know I should know the answer to this but it's been a while. I am working on a project that has a SLC5/05 and several Remote I/O panels. I have...
Replies
4
Views
2,414
Hi there, I'm wanting to connect a panelview 800 to an SLC5/03 the SLC is connected to an 1747-AIC which is run to another 1747-AIC. I'm trying...
Replies
0
Views
1,560
I have spent far too much time on this and not got communication working yet. Equipment: SLC 5/03 1747-L532 series C, Panelview Plus 600...
Replies
10
Views
4,111
Has anyone made a connection from a SLC to a Panelview 800, specifically using the 1761-NET-ENI interface. The literature says a connection to the...
Replies
6
Views
3,365
Back
Top Bottom