Ok hopefully this is an easy fix.
SLC 5/05 processor and a 1746-NO8I 8 channel analog output card.
Analog outputs are going to powerflex 4 drives.
Right now we are using channels 0-4 but we added another pump so now i am using channel 5 as well. I setup my pid and manual control in the program (all 0-16383) and got ready to fire it up. I checked the output and it was dead.... I had made all of my changes online so i thoguht maybe i needed to re-download for the changes to take effect. I went offline and redownloaded the program (rack stayed powered) and my output started working. somewhat.
the channel data format is set to scaled for pid and yet my output appears to be based on the NO4 data format.
example. if i give it a 16383 (should be 20mA in scaled for pid) i get a 10.5mA output. Thats what i would get if i was using the no4 format. Should i cycle power to the rack or is there something i am missing?
here ya go. its working now, but this is how its setup.
Similar Topics
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
259
I have a SLC500 5/05 and we have an alarm setup to monitor the status of the Analog Inputs we have wired to a 1746-NI8. We are using 5 of the...
Replies
14
Views
2,816
Hi, Sorry for my bad english, I'm from Poland. I've decided to learn basic PLC programming as hobby and to maybe get a better job. I have...
Replies
2
Views
1,338
Hello all, I'm having an issue displaying the value I'm getting from a PFC to display on my Red Lion G307..... and before anyone says it...I...
Replies
1
Views
2,134
Today while tracking down a 4-20 mA loop problem for old project since 2005. mA for loop is OK but channel give me -1 on scada i found rung...
Replies
5
Views
2,793
Back
Top Bottom