I have an SLC500 with what appears to be a chassis configuration fault (S:6 is showing 0056). Chassis is configured as follows:
Slot 0: 5/02 CPU
Slot 1: Analog Input
Slot 2: Digital Input
Slot 3: Digital Output

Is there a way to check to see if the modules are detected by the CPU? This is an existing system that has been working for a few years, so I'm thinking I will find one of the modules no longer works properly.

Thanks.
 
If you can go online with RSL500 I would create a new project, then do a read of the IO through RSLinx. If a module isn't seen by the PLC it wouldn't show up correctly.
 
Unfortunately I do not have RSL available at the moment since I'm in the field. I have access to a diagnostic panel that allows me to read and write registers. Is there a register that stores chassis configuration information?
 
I think that is deep in the internals of the processor, what you could get to in the S2 file would be the enable bits S:11/0 - S:11/15 that will turn off the control of the card, and checking of it.

If you turn off one bit at a time then try to run the program it might run without fault if the bad card is disabled.

But, if it's a rack problem it may effect all the cards.
 
Just a shot in the dark but.... try removing the terminals to the I/O cards and see if it clears, this will tell you if its a short in the field and shorting out a card

Also the power supplies on the SLCs are the weak link so if you have one try changing it first
 

Similar Topics

We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and...
Replies
21
Views
4,199
I need help in identifying the fault with a 1746-NR4 RTD / resistance module. The hardware is a SLC500 1746-NR4 module inserted into slot 3 of a...
Replies
0
Views
1,294
I'll try to be brief, long story short I'm tasked with bringing a packaging machine back from the dead that has a re-engineered control system...
Replies
14
Views
4,934
Just got back from a customer with an L40C (SER C, FRN 6) that immediately faults at powerup. I can download the program, switch to RUN, and it...
Replies
2
Views
1,681
Morning everyone! There’s a program for a machine I’m making some changes to. My questions are about other things in the program. SLC 5/05...
Replies
2
Views
1,652
Back
Top Bottom